Gateway datasheet says the 24 V digital inputs draw a ‘current load’. What does that mean for my sensors?

Gateway datasheet says the 24 V digital inputs draw a ‘current load’. What does that mean for my sensors?

Çözüldü 4 3

Student again. For a lab rig we have a gateway with 4 digital inputs that we want to use for a door contact, a float switch and two NPN proximity sensors, with the states going to Hermetry. The datasheet table says for the inputs:

Input type:       sinking, IEC 61131-2 type 1/3
On voltage:       > 11 V
Off voltage:      < 5 V
Input current:    3 mA @ 24 V ("current load")

Why would an input “load” anything, isn’t it just measuring voltage? Does the 3 mA matter for my wiring? Also the prox sensors are NPN and I think the input is sinking, which seems like it would not work?

♥ 0

Before the theory: check the gateway model actually supports what you plan with those inputs. Pulse counting on digital inputs depends on the model, for example.

♥ 0

We only need on/off states, no counting. Good to know though.

♥ 0

Fair questions, they confused me as well when I started.

The input deliberately draws a few mA when it’s on. An input that only “measured voltage” with a very high impedance would see 15 V picked up on a long cable next to a motor lead and call it ON. By needing 3 mA, a weak induced voltage can’t hold it up. That’s what the type 1/3 classes in IEC 61131-2 define: voltage and current ranges for ON and OFF.

It also matters for 2-wire sensors. A 2-wire prox still leaks a little current when it’s off. If that leakage is above what the input accepts as OFF, the input never turns off. Type 3 inputs are designed to tolerate that leakage, type 1 inputs may not be.

Your wiring: “sinking” input means current flows into the input and out to 0 V, so it needs a device that sources +24 V into it. That’s a PNP sensor or a dry contact between +24 V and the input. An NPN sensor pulls the input towards 0 V, so on a sinking input it does nothing. Options: buy PNP versions of the prox sensors (easiest), or use an interposing relay.

The door contact and float switch are dry contacts: wire them from +24 V to the input. 3 mA through a reed contact is fine.

On the Hermetry side send the states as 0/1 numbers so they can be charted and alarmed on.

Kabul edilen çözüm♥ 7

That explains it, thanks Ciaran. We swapped the NPN proxes for PNP ones (the lab had some), the door and float switch go from +24 V to the inputs, all four show 0/1 in Hermetry now.